joe tedesco
- Boston, Massachusetts
12.3.10 An individual terminal shall be provided for the connection of each branch-circuit neutral conductor.
 In what edition was this sentence first added?
Jim, I agree totally. In all the years of installiing panels, not once have I found listed or labelled instructions on how many conductors are required in terminals within the equipment. I believe Article 110.14(a) 1981 'Terminals' was the second time I witnessed an AHJ enforce the ruling of using a single conductor in a main panel grounded termination. That statement is still unchanged to this day in the 2008.jim dungar said:A UL listing/label only says the device built at the factory in accordance with the appropiate UL standard.
I know there are some installation standards (in particular NEMA), but I know of no UL standard that deals with "field" installation.
gndrod said:In all the years of installiing panels, not once have I found listed or labelled instructions on how many conductors are required in terminals within the equipment.
iwire said:Jim, an HVAC unit has a Label that specifies the MCA, MOP voltage etc.
IMO that label is part of the listing and labeling that 110.3(B) references.
	gndrod said:Jim, I agree totally. In all the years of installiing panels, not once have I found listed or labelled instructions on how many conductors are required in terminals within the equipment. I believe Article 110.14(a) 1981 'Terminals' was the second time I witnessed an AHJ enforce the ruling of using a single conductor in a main panel grounded termination. That statement is still unchanged to this day in the 2008.
gndrod said:Additionally, interpretation can go further to included grounding conductors as well, should an AHJ have a reason to enforce conductor termination safety. JMO rbj
joe tedesco said:Here's a picture of a panelboard for use concerning this discussion.
UL 67, 12.3.10 An individual terminal shall be provided for the connection of each branch-circuit neutral conductor.
jwelectric said:Yes I also agree that any UL standard is not part of the instructions included with the listing and labeling....
...Every panel I have installed had information on the label concerning the ground terminal bar....
...It was due to this debate that Jim Pauley made the proposal of one screw one neutral.
jim dungar said:I interpret Pauley's proposal as being an attempt to make the installation requirements (NEC) correspond to manufacturing requirements (UL). Because the NEC is generally a permissive code (if it doesn't say no then it is okay) and in your label example the singular form of the word "wire" only infers a limit of one conductor.
	jwelectric said:But to get back to the point of Standard 67, there are some educators out there that are teaching that to have two neutrals under one screw is a violation of 110.3(B) as outlined in UL Standard 67.
I contend that UL Standard 67 plays no role what so ever in the instructions included in the listing and labeling of a panel.
For Standard 67 to be quoted as a code violation the Standard would be required to be included with the panel when the panel was sold and not purchased separately at the price of $1000.
I interpreted that as well.jim dungar said:Bob,
I agree.
I did not mean to include "labels and instructions required as part of the UL Listing". I meant only to indicate the UL Label itself says the item was built to UL standards and does not specifically infer how to install or use the item.