Unbalance 3-phase current calculation

Status
Not open for further replies.

stevee

Member
Ok, probably a simple answer, or maybe not but let me ask anyhow.

On a typical 3-phase, 4-wire, 480/277v system with a 100A rated panelboard and a 100A rated main circuit breaker. The panelboard is used for lighting load operating at 480V.

The lights are single phase, 480V.

The connected load between phases A and B is 40A
The connected load between phases A and C is 30A
The connected load between phases B and C is 30A

What would the current be on the conductors supplying power to the panelboard?

In other words with the above connected loads...
A phase would draw _____ amps?
B phase would draw _____ amps?
C phase would draw _____ amps?

Is there a simple formula to calculate the individual currents on each phase?
 

skeshesh

Senior Member
Location
Los Angeles, Ca
Just think of it as a semi-panel schedule. 40A@480V(single phase)=19200VA and 30A@480V(single phase)=14400VA. Divide the watts up between phases like you would do in a panel schedule, i.e. if there's 19200VA between phases A & B then under each phase column would get 19200/2=9600VA. Add up the VA for each phase till you get a subtotal for each phase then divide by L-N voltage and get the load current on each phase.
 

mithun46

Member
can you explain it some more clearly?????????

Please post the entire solution for the above problem if possible.
 

kwired

Electron manager
Location
NE Nebraska
I believe the balanced portion of the load will be 30 amps / 1.73 so 17.34 per phase for the balanced load.

You then have 10 amps unbalanced between A and B

A=27.34
B=27.34
C=17.34
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I believe the balanced portion of the load will be 30 amps / 1.73 so 17.34 per phase for the balanced load.

You then have 10 amps unbalanced between A and B

A=27.34
B=27.34
C=17.34

I think you mean 30 amps * 1.73 so 51.96 per phase for the balanced load.

I come up with:

A=60.83
B=60.83
C=51.96

This presumes that the power factor is the same for all three loads so that the phase currents are 120 deg apart.
 

stevee

Member
Just think of it as a semi-panel schedule. 40A@480V(single phase)=19200VA and 30A@480V(single phase)=14400VA. Divide the watts up between phases like you would do in a panel schedule, i.e. if there's 19200VA between phases A & B then under each phase column would get 19200/2=9600VA. Add up the VA for each phase till you get a subtotal for each phase then divide by L-N voltage and get the load current on each phase.

I think this method makes the most sense to me.

Using this method the current comes out to be:
40A x 480 = 19,200W / 2 = 9,600W
30A x 480 = 14,400W / 2 = 7,200
Total Load connected to Phase A = 16,800W
Current Phase A = 16,800/277 = 60.6A

Does anyone know of a reference that this calculation could be found in?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I think this method makes the most sense to me.

Using this method the current comes out to be:
40A x 480 = 19,200W / 2 = 9,600W
30A x 480 = 14,400W / 2 = 7,200
Total Load connected to Phase A = 16,800W
Current Phase A = 16,800/277 = 60.6A

Does anyone know of a reference that this calculation could be found in?

This method provides a close approximation in this case, Ia=60.65, Ib=60.65, Ic=51.99, as compared to using the calculation Ia=Iab-Ica (etc.) which gives Ia=60.83, Ib=60.83, Ic=51.96.

However, the larger the unbalance, the larger the error. For instance, with Iab=40, Ibc=30 and Ica=10, the shortcut method would give Ia=43.32, Ib=60.65 and Ic=34.66, but the calculation method would give Ia=45.83, Ib=60.83 and Ic=36.05.

You can see with the larger imbalance the shortcut method gives a line A current which is off by 2.5A, and the line C current is off by almost 1.5A.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
The equations are derived from the standard single phase/pole power equation.

View attachment 5210

The 1.15 for a 2-pole load, some may refer to as the mythical Oregon Fudge Factor.

But it's really pretty straight forward math. Until you try the symmetrical components....
 

kwired

Electron manager
Location
NE Nebraska
I think you mean 30 amps * 1.73 so 51.96 per phase for the balanced load.

I come up with:

A=60.83
B=60.83
C=51.96

This presumes that the power factor is the same for all three loads so that the phase currents are 120 deg apart.

You are correct. Except I don't know where 60.83 comes from shouldn't it be 61.96 for A and B?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
You are correct. Except I don't know where 60.83 comes from shouldn't it be 61.96 for A and B?

It wouldn't be 61.96. If the current from A-B = 40<0, from B-C = 30<-120 and from C-A = 30<-240, then using KCL Ia=Iab-Ica.

Or, Ia= (40<0) - (30<-240)

Ia= (40+j0) - (-15+j25.98)

Ia= 55 - j25.98

Ia= 60.83<-25.28
 