kookyburns1952
New member
Bear with me on this, I'm a student. I'm using Holt's Study Guide Volulme 1 for the NEC 08, page 100.
To determine conductor sizes for a 200 amp load I've multiplied by 125% for the ungrounded conductors and 100% for the grounded conductor. The study guide then asks the question about sizing the grounded conductor based on the 50 amp unbalanced load. Where do they get the 50 amp unbalanced load from? The only thing I see is the difference between the multiplying for the ungrounded conductor size and the grounded conductor size; 250 - 200=50. Please define the unbalanced load so a student can understand. The textbook gives these examples throughout, but leaves me confused at times. The unbalanced load is used then to determine the minimum grounded conductor size from table 250.122. A def on balanced load would also be helpfull.
To determine conductor sizes for a 200 amp load I've multiplied by 125% for the ungrounded conductors and 100% for the grounded conductor. The study guide then asks the question about sizing the grounded conductor based on the 50 amp unbalanced load. Where do they get the 50 amp unbalanced load from? The only thing I see is the difference between the multiplying for the ungrounded conductor size and the grounded conductor size; 250 - 200=50. Please define the unbalanced load so a student can understand. The textbook gives these examples throughout, but leaves me confused at times. The unbalanced load is used then to determine the minimum grounded conductor size from table 250.122. A def on balanced load would also be helpfull.