Is there a burial depth for conduit in concrete that is inside a building not in contact with the earth? Think of a slab on a2nd floor of a commercial building.
Like what? That is what I am trying to figure out. I have not see anything that would pertain to say a conduit trenched in across a floor to be covered by say 2" concrete--- Maybe protection could be used? IDKIMO, it is not buried at all if it is not in contact with earth.
On the other hand, there are various rules about concrete encasement that might apply.
I think if you were a little more forthcoming in explaining what it is you want to do, it might be easier to give you an answer.
As long as the wiring method allows you to put it in concrete, you are good to go as far as I can tell UNLESS it is a structural issue. Then you would need permission from the guy that designed the structure.Not a real situation but suppose I need to trench a branch circuit across a floor where there were half walls. Perhaps drilling thru the floor was not an option so how could I compliantly go from one half wall to the other?
So 1/2" under the concrete is fine? That is what I think but it seems wrong.As long as the wiring method allows you to put it in concrete, you are good to go as far as I can tell UNLESS it is a structural issue. Then you would need permission from the guy that designed the structure.
300.5 is for underground.IMHO, the only thing I can recall is the requirement for Service Conductors and also 300.5
I don't see any obvious issues with it. It would be legal to just run it along the floor.So 1/2" under the concrete is fine? That is what I think but it seems wrong.
Yeah that would go over well....hahaI don't see any obvious issues with it. It would be legal to just run it along the floor.
why not? you could run it in the corners where no one would trip on it.Yeah that would go over well....haha
Service conductors need to be encased in at least 2 inches of concrete to be considered outside the building regardless of whether concrete is a slab, slab on grade, or other encasement.IMHO, the only thing I can recall is the requirement for Service Conductors and also 300.5
Might be. Put it this way it is fine with NEC, structural design purposes, might weaken the slab depending load characteristics designed into the slab and how and where in the slab you want to do this particularly when not a slab on grade.So 1/2" under the concrete is fine? That is what I think but it seems wrong.
Good idea IMO for on grade slabs anyway.300.5 has a row for "under a building" and the required depth is "0". I see that as saying it can be in the floor slab with the top of the raceway level with the finished floor. Any depth greater than that is permitted, either in the slab itself or below the slab. Note that the engineers often have requirements for raceways in the slab that either prohibit them or restrict the size and location to help avoid cracks in the concrete.
The specs of most of my jobs required my conduits to be in the fill below the slab and not in the slab itself.
1/2", 1/4" 1/8", etc. doesn't matter. T300.5 does not apply.So 1/2" under the concrete is fine? That is what I think but it seems wrong.
I seem to recall that section titles are not part of the code, or at least are not enforceable.I agree with all that the table doesn't apply because section 300.5 is called underground installations
So we can ignore the fact that art 422 applies to appliances, 430 to motors, 440 to air conditioning or 210 to branch circuits, 215 to feeders and 230 to services and probably many others that narrow down what it applies to and just pick and choose what we want to use?I seem to recall that section titles are not part of the code, or at least are not enforceable.
You can ignore the TITLES, but not the text. The first paragraph of each code article tells you what the article applies to.So we can ignore the fact that art 422 applies to appliances, 430 to motors, 440 to air conditioning or 210 to branch circuits, 215 to feeders and 230 to services and probably many others that narrow down what it applies to and just pick and choose what we want to use?
Can I choose to use 300.5 for overhead conductor clearances?