davidlbriggs
Member
- Location
- Asheville, TN
- Occupation
- Electrical Design Engineer
Under NEC 2017, can residential electric ranges be hard wired? Does UL 858 allow? If so is no GFCI required? Has TIA 1563 been accepted?
Hard wiring would under NEC 110.3 B
In 210.8 is the requirement for GFCI protection for outlet or receptacle?
I don’t have access to UL 858 nor the TIA status
This requirement shall become effective on January 1, 2023 for mini-split-type heating/ventilating/air-conditioning (HVAC) equipment and other HVAC units employing power conversion equipment as a means to control compressor speed.
Informational Note: Power conversion equipment is the term used to describe the components used in HVAC equipment that is commonly referred to as a variable speed drive. The use of power conversion equipment to control compressor speed differs from multistage
compressor speed control.
maybe the correlating committee could host a few 3 martin luncheons Don? ~RJ~Proposed TIA 1563 was not passed. It did not pass ballot at CMP2. There have been a couple of GFCI TIA proposals that passed ballot at CMP2 but did not at the correlating committee. As far as I know the only one to pass at both CMP2 and the CC, and was issued by the Standards Council is 1593.
That TIA added the following language to 210.8(F).
That why I asked if the GFCI protection is required for outlet or receptacle, no code book handyTom I don't think a hard wire residential range is required to have gfci protection.
The issue with ranges and ovens and tripping GFCIs is a temporary issue. The problem is that the calrod heating elements take on moisture on the long sea voyage to the US. When you first turn them on, the moisture permits enough ground fault current to flow and the GFCI trips. If you run all of the elements on high for 20-30 minutes with a standard breaker the problem will go away and then you can connect them to the GFCI.
The problem is who is going to pay for all of that extra work. I had a discussion with a NEMA rep at the eastern section meeting and he was telling me about a 400 unit apartment complex where they have this exact issue with all of the electric ranges.
Isn't the gfci requirement only for receptacles within 6' of a sink?
See post #12That’s what I was thinking.
Sent from my iPhone using Tapatalk
apparently a solid vs cord cap egcThe OP stated that this is a residential range (I would assume in a dwelling) under the 2017 so what is the issue?
Post #10 implies that he wants to know if it is permissible to not provide GFCI protection if the unit is hardwired. I don't know what you mean about the type of EGC being relevant.apparently a solid vs cord cap egc
~RJ~