Article 400.8 prohibit flexible cords in floors. Is it one of the leniencies of 645 to allow this (I don't see it)? Or is it implied given that you are allowed to put receptacles under the floor per 645.5(D)(2)?
In general how do we get away with a typical 645 application where your NEMA plugs are in boxes resting on the structural floor. i.e. beneath the raised floor.
Isn't the allowance of receptacles under the floor per 645 redundant in that they are allowed regardless? i.e. The problem in all scenario's is installing flexible cords such that the receptacles are useful.
Mike
In general how do we get away with a typical 645 application where your NEMA plugs are in boxes resting on the structural floor. i.e. beneath the raised floor.
Isn't the allowance of receptacles under the floor per 645 redundant in that they are allowed regardless? i.e. The problem in all scenario's is installing flexible cords such that the receptacles are useful.