Underground Al Service Insulation damage

Location
Seattle
Occupation
Electrician
Underground service wires were damaged by ditchwick. Two had to be spliced. The neutral has a nick in the casing down to the conductor but has not damage the conductor.

Is it better to squeeze deox into the insulation, then tape. Or cut the wire and splice with a Polaris NSIISPBS350 2P
 
Depending on soil alkalinity, aluminum can corrode severely in a short time. I have seen the situation you describe cause the conductor to open in only a few weeks. I have a feeling that electrolysis caused by the voltage on the exposed conductor to ground accelerated the corrosion. That conductor should have been treated the same as the other two current carrying conductors even though the conductor itself wasn't cut or it was the neutral.

-Hal
 
We would Scotch Kote bruised insulation then tape and repeat. Nicks that extended to conductor, the same treatment if we did it with a shovel while cleaning out the trench. Anything that had been there for moisture to enter, compression splice and heat shrink. We were starting to use Gel wraps more often.
 
It will fail in short time unless spliced with the correct underground splice. I had a client that lost one leg to a barn. I made it so he could just use the other leg since he didn't have any 240V loads. It was probably 2 weeks later he called and said he lost all power.
I located the bad section. Turns out the conductors were hit when a fence was put in.

Moral of the story, any Al wire damaged underground will fail in short order unless spliced and sealed.
 
WE located several faults in a feeder to an irrigation well. The well guys said they would repair but complained there was no damage at one location. I felt along it until I found a small hole on the bottom side, cut, stripped and showed them the damaged conductor. They replaced the entire length. If we took the time to flag, we could be within 1/4 to 1/2 inch depending on the depth.
 