I recalculate the ampacity for 3*4/0 copper XHHW 2*7 conduits of 2”
First, the maximum temperature in duct may be 90oC if in the air will be as per Table 310.16 for 75oC.
So, for 5.5" distance center line-to-center line, 60% load factor, the ampacity will be 200 A.
First, the maximum temperature in duct may be 90oC if in the air will be as per Table 310.16 for 75oC.
So, for 5.5" distance center line-to-center line, 60% load factor, the ampacity will be 200 A.