Re: underground ducts
I appreciate the comments. I want to clarify that I was not responsible for the situation, or that I would put in anything other than UL listed and labeled electrical conduit for the instalation. This pipe is in the ground and was available. I was asked if I thought it met NFPA. I think that 310-60.(a) is ment to allow abandoned pipe to be used for the installation of direct buried rated cable as long as the pipe is below the direct buried depth. If above that depth the cable must be installed in listed electrical conduit. I know that is a fine line, but so is conduit embedded in a concrete wall. Other considerations would be where the conduit exits the ground i.e. plenum areas etc.
I appreciate the comments. I want to clarify that I was not responsible for the situation, or that I would put in anything other than UL listed and labeled electrical conduit for the instalation. This pipe is in the ground and was available. I was asked if I thought it met NFPA. I think that 310-60.(a) is ment to allow abandoned pipe to be used for the installation of direct buried rated cable as long as the pipe is below the direct buried depth. If above that depth the cable must be installed in listed electrical conduit. I know that is a fine line, but so is conduit embedded in a concrete wall. Other considerations would be where the conduit exits the ground i.e. plenum areas etc.