When running Rigid Metal Conduit, 300.5 “does not” clarify if the 90 degree transition from a rigid horizontal run to vertical SCH 80 (emerging) has to be a 90 Rigid Metal Conduit or if it can be PVC?
Since it does not state anything about the 90 whatsoever when transitioning from horizontal rigid metal conduit to vertical SCH 80, I assume it can be either.
I am thinking 300.5(D)(4) gives permission for the 90 to be PVC since it mentions SCH 80.
Can the 90 be PVC, and what part of 300.5 proves this point?
If you are going to run RMC underground, why not just run RMC the full length? Or am I misunderstanding your setup?
Usually it would be PVC underground, and conservatively if needed, RMC sweeps, and RMC risers, bonded at their respective terminal enclosures.