Underground Junction Box Sizing

Merry Christmas
Status
Not open for further replies.

paulgarett

Member
Location
San Rafael, CA
Do underground junction boxes follow the guidelines required in NEC 314.28(A)(1) and (2)?
314.28: Pull and Junction Boxes and Conduit Bodies
314.28 (A) Minimum Size
314.28 (A) (1) Straight Pulls and (2) Angle or U Pulls
and 312.6(A) opposite removable cover

Two pairs of 2 inch PVC conduit will enter an underground j-box. Will distance between each pair of conduits follow the above NEC guidelines 314.28(A)(1) or (2) or possibly 312.6?
If the underground j-box is positioned in a way so that the conduit enter the j-box from the side or the corner, then should the size of the j-box should be sized accordingly?
 
Do underground junction boxes follow the guidelines required in NEC 314.28(A)(1) and (2)?
314.28: Pull and Junction Boxes and Conduit Bodies
314.28 (A) Minimum Size
314.28 (A) (1) Straight Pulls and (2) Angle or U Pulls
and 312.6(A) opposite removable cover

Two pairs of 2 inch PVC conduit will enter an underground j-box. Will distance between each pair of conduits follow the above NEC guidelines 314.28(A)(1) or (2) or possibly 312.6?
If the underground j-box is positioned in a way so that the conduit enter the j-box from the side or the corner, then should the size of the j-box should be sized accordingly?

IMHO a J-box is a J-box. Location is a different story...
 
Do underground junction boxes follow the guidelines required in NEC 314.28(A)(1) and (2)?
314.28: Pull and Junction Boxes and Conduit Bodies
314.28 (A) Minimum Size
314.28 (A) (1) Straight Pulls and (2) Angle or U Pulls
and 312.6(A) opposite removable cover

Two pairs of 2 inch PVC conduit will enter an underground j-box. Will distance between each pair of conduits follow the above NEC guidelines 314.28(A)(1) or (2) or possibly 312.6?
If the underground j-box is positioned in a way so that the conduit enter the j-box from the side or the corner, then should the size of the j-box should be sized accordingly?

Yes, Handhole enclosures (Underground junction boxes) must be sized in accordance wtih 314.28(A). See 314.30(A)

Chris
 