roncom0351
Member
- Location
- South East Texas
I have a situation where two underground circuits #1 (2 runs of 1300 LF of 1 Ph 250 THWN in 3") #2 (2 runs of 1300 LF of 1 Ph 1/0 THWN in 2") located in the water table (water is present in MH's) does not pass a megger test. The original runs did not pass so the conductors were removed and new conductors installed. (Getting the same results).
I'm being told by the contractors engineer that the cables are not passing because of the water the cable is in.
The first test on the original cable pulls did not pass the megger testing so the contractor applied 120 volts to heat up the cables and try to dry the moisture out. This didn't work.
Both of the second set of conductors are not passing the megger testing.
The contractor is asking us to approve letting them power up the cables without the testing complete.
I have only run into this situation a long time ago when the cables came with paper/insulation wire covering.
The new cables these days don't have the paper covering and should not have moisture in the wire.
Does anybody have suggestions as what to do to get these new cables to pass the megger testing.
I'm being told by the contractors engineer that the cables are not passing because of the water the cable is in.
The first test on the original cable pulls did not pass the megger testing so the contractor applied 120 volts to heat up the cables and try to dry the moisture out. This didn't work.
Both of the second set of conductors are not passing the megger testing.
The contractor is asking us to approve letting them power up the cables without the testing complete.
I have only run into this situation a long time ago when the cables came with paper/insulation wire covering.
The new cables these days don't have the paper covering and should not have moisture in the wire.
Does anybody have suggestions as what to do to get these new cables to pass the megger testing.