A 600V street lighting system that gets to be a ½ mile long is a essentially going to behave like a transmission line and the public safety issue is not really addressed other than in 110.10 of the NEC because they are not that common.
You basically run into the situation where a 600V breaker may not be able to properly operate in a fault condition.
The most common feeder / transmission line faults are a single-phase faulting to ground.
Case law clearly indicates FDOT would be found liable if a person encountered a hazardous voltage on the ground around one of the pull boxes from such a ground fault, regardless of if the NEC requires it.
I linked several law cases above, where an plaintiff has been killed from a energized man hole.
I believe FDOTS engineers need to do their due diligence to ensure the public is protected from a ground fault along that feeder.