Underground PVC size transition

Status
Not open for further replies.
What is the length of the 2" 'sleeve'?

As I understand it, the reason you can't simply slide some 1.25" through the 2" sleeve is because of the bell ends for joining lengths of 1.25". But if you had a long enough length of 1.25" you would have no problem, correct?

Would a flexible NM raceway be suitable for the entire run, something continuous with no joints in the middle?

-Jon

He could pull 1.25" carflex/NMLTFC through the 2" PVC, but then would have to transition it underground. I don't think NMLTFC connectors are suitable for direct burial even though the conduit itself is.
 
I'd bring the 2" up out of the ground on the house side into a conduit body or pullbox and use one of those bushings iwire pointed out on the garage side. Send a fishtape in from the garage side (go from smaller into larger conduit) and pull in a pullrope. Then pull the wire in, going from smaller into larger again. Shouldn't have an issue getting through the reducing bushing if you pull it that way.
 
... your trench should have been at 24 inches and not 18 inches.

:ashamed:Just double checked Table 300.5, column 3. You are correct. I believe the pipe is at least 24" deep under the driveway since it arcs down and then up. Where I connect, it's 18" deep about 3' from edge of driveway.
 
What is the length of the 2" 'sleeve'?

As I understand it, the reason you can't simply slide some 1.25" through the 2" sleeve is because of the bell ends for joining lengths of 1.25". But if you had a long enough length of 1.25" you would have no problem, correct?

Would a flexible NM raceway be suitable for the entire run, something continuous with no joints in the middle?

He could pull 1.25" carflex/NMLTFC through the 2" PVC, but then would have to transition it underground. I don't think NMLTFC connectors are suitable for direct burial even though the conduit itself is.


The 2" sleeve is about 60' long. Using a continuous length of liquidtight is an awesome idea. I have buried those liquidtight connectors before. I assumed they were direct burial since the conduit is. Need to check that.
 