Underground servcie entrance

Status
Not open for further replies.
iwire said:
You can not bring type USE into the building.

What about when used as the 4th wire EGC as part of a URD8000 3 wire feeder (Which is allowed to be brought into a premisis) and terminated nearest the point of entry?
 
A/A Fuel GTX said:
What about when used as the 4th wire EGC as part of a URD8000 3 wire feeder (Which is allowed to be brought into a premisis) and terminated nearest the point of entry?

Is it bare?

As I understand it straight USE is not flame retardant
 
iwire said:
Dennis no exception necessary.

I am trying to understand why we are allowed to use USE inside if it is dual rated. Wouldn't the NEC have to state that? As it stands now the NEC does not allow USE inside-- at least from what I can see.
 
Dennis Alwon said:
I am trying to understand why we are allowed to use USE inside if it is dual rated. Wouldn't the NEC have to state that? As it stands now the NEC does not allow USE inside-- at least from what I can see.

Dennis, from what I can gather, it is related to the insulation being flame retardant and many of the newer USE's have the RHW-2 designation which allows it to be brought inside, IMHO
 
A/A Fuel GTX said:
Dennis, from what I can gather, it is related to the insulation being flame retardant and many of the newer USE's have the RHW-2 designation which allows it to be brought inside, IMHO

I totally agree but where is that permission given that says if USE is flame retardant we can use it in the interior of a building.

UL says that non dual rated has not been tested for a vertical flame rating thus it is not allowed in the interior. Because dual rated USE has been tested for use inside does not necessarily allow us to use it there.
 
I guess I'll answer your question with a question. If the insulation IS flame retardant, why would it not be allowed to brought inside?
 
Dennis Alwon said:
I totally agree but where is that permission given that says if USE is flame retardant we can use it in the interior of a building.

UL says that non dual rated has not been tested for a vertical flame rating thus it is not allowed in the interior. Because dual rated USE has been tested for use inside does not necessarily allow us to use it there.

Dennis the fact that it is USE / RHW is all the permission you need.

If it has both ratings it meets the requirements for both
 
iwire said:
Dennis the fact that it is USE / RHW is all the permission you need.

If it has both ratings it meets the requirements for both

I see your point. I can't get over the fact that it is still USE...... I guess I will have to get over it. ;)


A/A Fuel GTX said:
I guess I'll answer your question with a question. If the insulation IS flame retardant, why would it not be allowed to brought inside?

I agree it should be allowed but again the code doesn't state this. I agree logic should prevail but tell that to the judge.:grin:
 
Dennis Alwon said:
I see your point. I can't get over the fact that it is still USE......

It is USE that is also RHW it can not be labeled RHW if it is not flame retardant.

I agree it should be allowed but again the code doesn't state this. I agree logic should prevail but tell that to the judge.:grin:

Dennis it does not have to state it, RHW is OK for indoors and they could not stick the RHW label on a conductor that does not meet the standards for RHW.

You run into the same thing all the time with dual rated THHN/THWN.

THHN can not be run in wet locations but THWN can be.:smile:
 
Dennis Alwon said:
. . . I can't get over the fact that it is still USE. . .
OK, cut a bunch of small pieces of masking tape and place them over the letters "USE" everywhere they are exposed inside the building. Have a glass of wine, a bite of cheese, put on some soft music, relax for a little while, then get back to work and stop this foolishness. :D
 