Underground service entrance conductors

Status
Not open for further replies.

muckusmc

Senior Member
Location
Roebling, NJ
2005 Code - Is it legal to run parallel runs of 500MCM/USE cables in the same trench without installing same in conduit??
I couldn't find anything in the code saying no but am wondering if I missed something.
Thanks,
Muck
 
masterinbama,
Thanks for the response.
Was hoping that was the case - saves alittle bit on conduit and the trouble of trying to coordinate with the POCO.
Thanks again.
 
I prefer conduit because excavators are always digging up stuff. Conduit gets broken but the conductors usually make it. Make sure you use a red tape 12 inches over the conductors to warn people that there are live wires down there.
 
Yes, you can install them in the same trench, but if you do the derating factors in Table 310.15(B)(2)(a) apply.
 