Re: underground service
Originally posted by sparks1:
One way distance is the distance from the supply to the load (just "one way")I based my calculation on the one way distance given from the link , assuming this means out and back to the load.
i.e. the length of just one of the conductors.
It's not out and back.
Originally posted by sparks1:
I don't know why you would figure Vd for a totally unbalanced load (i.e. for just 120V), since that's pretty unlikely. All of your 240V loads are balanced automatically. And 120V loads on different phases balance each other.I used 120v for maximum unbalance on the neutral not 240v since these loads are balanced.
If you mean that you aren't counting any 240V loads, then your Vd calc will be off because you aren't looking at the total amperage on each wire.
If you are using a fused source, and one fuse blows, all 240V loads will drop off. Do you think that you will still have 100A of 120V load left running under that scenario?