underground splice of lamp post UF

Status
Not open for further replies.

PowerLimited

Member
Location
Bugtussle
How advisable and viable if at all is an underground splice of UF cable (that has a ground fault, near the post I would bet) supplying a residential outside lamp post ? (a tree incident banged the lamp post pretty good, and may have driven post downward enough to damage the UF cable causing a ground fault. In any case, there is a ground fault somewhere in the secion of cable between the house and the lamp post).

Are 'underground splice' products reasonably practical and reliable and compliant ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
They work well if you follow the instructions. We prefer the strecher type which are about 12" long so you may remove a section of damaged cable. Stretcher type is on the right in the photo, it basically gives you more cable to work with.

mediawebserver
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
I didn't end up using them, but a couple weeks ago I purchased some splices that were self-soldering, sort of. They looked like butt splices, but you put the wire in, apply heat from a gun or blow-dryer and the solder/flux would melt around the wire. Three of those, plus cover it with shrink-tubing and you should be good to go.
 