I insparks Member Feb 5, 2009 #1 I need to know if romex in a conduit ran under a slab is okay, I think it should be rated UF but the inspectors around here say it's okay and allow it. So who is right? Thanks in advance.
I need to know if romex in a conduit ran under a slab is okay, I think it should be rated UF but the inspectors around here say it's okay and allow it. So who is right? Thanks in advance.
V Volta Senior Member Location Columbus, Ohio Feb 5, 2009 #3 M. D. said: not compliant Click to expand... 'cause it's a wet location. 300.5(B). 2008.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Feb 5, 2009 #4 Inside a conduit is not a location. If the conduit is in a wet location, so are the conductors within.
Inside a conduit is not a location. If the conduit is in a wet location, so are the conductors within.
weressl Esteemed Member Location Texas by the Gulf, geat crab, great shrimp Feb 5, 2009 #5 Volta said: 'cause it's a wet location. 300.5(B). 2008. Click to expand... Is it to be consdiered wet in Death Valley?
Volta said: 'cause it's a wet location. 300.5(B). 2008. Click to expand... Is it to be consdiered wet in Death Valley?
billsnuff Senior Member Location East of 480sparky Feb 5, 2009 #6 good question good question Is it to be consdiered wet in Death Valley? Click to expand... death valley data - temp and rain http://www.wrcc.dri.edu/cgi-bin/cliF302000.pl?cadeat