Customer wanted to change out every single duplex receptacle to a 2 gang duplex receptacle, problem is its looks like AWG 16 for ground. No attic or crawl space access to comply with 250.130 (c) without some major removal of walls then I might as well just abandon them and surface mount receptacle were he needs.
I got a call into local AHJ to see if he will allow anything since I am not "extending" the circuit.
Any liability you see ( if AHJ allows) in just using what's there since at one time it was compliant.