The panel having 150 amps doesn't mean that all of that amperage is being used, nor being used all the time. Also the generator may only be for emergency/power outages, in which case the power usage can be kept to a minimum of only essentials. A question for you: Is it a 65 AMP generator or a 65 KVA?My friend has a 16kw whole-house generator. Her house is 2,000 sf with a 3-ton air conditioner, washer, dryer, range, pool pump, and irrigation pump. How can all this, which comes off of a 150A service, be run on a 65A generator?
Sent from my SM-G935P using Tapatalk
150 amps being available doesn't mean that all of those amps are being used by the home, nor being used all the time. The actual average usage could be lower than the generator rating.My friend has a 16kw whole-house generator. Her house is 2,000 sf with a 3-ton air conditioner, washer, dryer, range, pool pump, and irrigation pump. How can all this, which comes off of a 150A service, be run on a 65A generator?
Sent from my SM-G935P using Tapatalk
I actually prefer your answer to mine.Whole house generators are always undersized compared to the service the home has. The assumption comes from the fact that you won't be doing laundry, cooking a thanksgiving turkey and have every light on at the same time. Also, a home very rarely uses 100% of the service it has. I bet the average load on the home is around 80 amps or so give or take. Sizing a generator to supply 100% of the homes "possible" load would be cost prohibitive.
Sent from my VS987 using Tapatalk
Well, it got us through Irma. Thanks for the input.
Sent from my SM-G935P using Tapatalk
If your POCO meter also measures maximum demand, you can use that figure to check the size of your generator. However, the size of the generator need to be much bigger than that if you are block loading the generator ie putting all loads at once on the generator instead of applying the load gradually.
What about having an inverter AC to solve the generator starting problem ? Of course, the running load i/c AC should not exceed generator rating ie 7kW.The only load I have in my house that could be problematic is the AC. It's on a 40 DP breaker, and the panel buzzes nicely every time it turns on. I could manage every load except AC on a 7kW unit without difficulty.
A question for you: Is it a 65 AMP generator or a 65 KVA?
What about having an inverter AC to solve the generator starting problem ? Of course, the running load i/c AC should not exceed generator rating ie 7kW.
We are talking about newer AC units, especially mini splits, which have a built in VFD to run the compressor at partial power for added efficiency. The soft start is a bonus of that design.
Sent from my XT1585 using Tapatalk
Not the design standard yet, in that it costs more. But available in almost all sizes and types for a price.Is that the design standard now? Even for non-split units?
Not the design standard yet, in that it costs more. But available in almost all sizes and types for a price.