I don't do much residential anymore and I'm trying to understand how to label and do my grounding/bonding for my the electrical system emergency disconnect for a single family dwelling fed by feeders.
This is a farm house. the utility supplies a meter and service disconnect at a pole about 75 ft from the house.
there is a 200amp main lug panel fed with four wires from the service disconnect on the utility pole.
this main lug panel feeds another 100amp panel on the outside of the house.
since the house is fed with feeders I would use 225.41 and label the 100 amp panel on the outside of the dwelling emergency disconnect.
does the service disconnect at the pole also need to be labled emergency disconnect, service disconnect?
im assuming my grounding and bonding would all be the same.
the poco provided meter/ service disconnect would need to have a gec connected to two ground rods and have the grounded/ grounding conductors bonded
the 200a main lug panel on the back side of utility pole fed with four wires would have grounded and grounding conductors isolated
the 100a main disconnect panel on the outside of the dwelling fed with four wires would have grounded and grounding conductors isolated. Because this is a seperate structure i would require one more ground rod at this location.
the dwelling has a metal undergroundwater piping system where the main line comes in. can i bond this anywhere on the metal water pipe back to the sub panel ground bar? 250.104(3) i would size the bonding jumper using 250.102(c) looks like if the panel is fed with 1/0 i can get away with running #6 copper to the water pipe?
I really appreciate all of you in this forum and would like to thank anyone in advance who replies or offers any input! hopefully I'm understanding the nec correctly and have a solid plan... thanks again!
This is a farm house. the utility supplies a meter and service disconnect at a pole about 75 ft from the house.
there is a 200amp main lug panel fed with four wires from the service disconnect on the utility pole.
this main lug panel feeds another 100amp panel on the outside of the house.
since the house is fed with feeders I would use 225.41 and label the 100 amp panel on the outside of the dwelling emergency disconnect.
does the service disconnect at the pole also need to be labled emergency disconnect, service disconnect?
im assuming my grounding and bonding would all be the same.
the poco provided meter/ service disconnect would need to have a gec connected to two ground rods and have the grounded/ grounding conductors bonded
the 200a main lug panel on the back side of utility pole fed with four wires would have grounded and grounding conductors isolated
the 100a main disconnect panel on the outside of the dwelling fed with four wires would have grounded and grounding conductors isolated. Because this is a seperate structure i would require one more ground rod at this location.
the dwelling has a metal undergroundwater piping system where the main line comes in. can i bond this anywhere on the metal water pipe back to the sub panel ground bar? 250.104(3) i would size the bonding jumper using 250.102(c) looks like if the panel is fed with 1/0 i can get away with running #6 copper to the water pipe?
I really appreciate all of you in this forum and would like to thank anyone in advance who replies or offers any input! hopefully I'm understanding the nec correctly and have a solid plan... thanks again!