understanding 230.85 /225.41 amd 225.42 grounding and bonding.
Necnerd
colorado
ME
I don't do much residential anymore and I'm trying to understand how to label and do my grounding/bonding for my the electrical system emergency disconnect for a single family dwelling fed by feeders.
This is a farm house. the utility supplies a meter and service disconnect at a pole about 75 ft from the house.
there is a 200amp main lug panel fed with four wires from the service disconnect on the utility pole.
this main lug panel feeds another 100amp panel on the outside of the house.
since the house is fed with feeders I would use 225.41 and label the 100 amp panel on the outside of the dwelling emergency disconnect.
does the service disconnect at the pole also need to be labled emergency disconnect, service disconnect?
im assuming my grounding and bonding would all be the same.
the poco provided meter/ service disconnect would need to have a gec connected to two ground rods and have the grounded/ grounding conductors bonded
the 200a main lug panel on the back side of utility pole fed with four wires would have grounded and grounding conductors isolated
the 100a main disconnect panel on the outside of the dwelling fed with four wires would have grounded and grounding conductors isolated. Because this is a seperate structure i would require one more ground rod at this location.
the dwelling has a metal undergroundwater piping system where the main line comes in. can i bond this anywhere on the metal water pipe back to the sub panel ground bar? 250.104(3) i would size the bonding jumper using 250.102(c) looks like if the panel is fed with 1/0 i can get away with running #6 copper to the water pipe?
I really appreciate all of you in this forum and would like to thank anyone in advance who replies or offers any input! hopefully I'm understanding the nec correctly and have a solid plan... thanks again!
No it's not an emergency disconnect it's the service disconnect.
Yes, normal service disconnect rules would apply, GEC connection, MBJ, etc.
Yes.
Yes.
the dwelling has a metal underground water piping system where the main line comes in. can i bond this anywhere on the metal water pipe back to the sub panel ground bar? 250.104(3) i would size the bonding jumper using 250.102(c) looks like if the panel is fed with 1/0 i can get away with running #6 copper to the water pipe?
No, since it qualifies as an electrode the connection needs to be within 5' of where it enter the structure. The correct table for a GEC is 250.66.
Yes.
Thank your for clarifying I really appreciate the help!
So because the metal water pipe is considered an electrode I need to make the connection within 5ft of it entering the dwelling using 250.66.
the house emergency disconnect is fed with 1/0 largest ungrounded conductor.
I should be able to run #6 from
building or structure disconnecting means enclosure where located at the building or structure
Equipment grounding conductor run with supply conductors
One or more grounding electrodes- the ground rod at the emergency disconnect on the outside of the house?
Or do I have to get 6 all the way out to the service disconnect at the pole?
I would also need to install an I interbonding system on the 100amp emergency disconnect on the outside of the house?
Yes when your replacing a grounding electrode system (GES) on an existing dwelling with existing communications systems ( CATV / Phone / satellite / random antennas ) those grounds should be moved to your new GES. There should be only one GES per structure, if any of the communications utilities drove their own little ground rod as they tend to do abandon that in favor of your new grounding system.
Yes when you’re replacing a grounding electrode system (GES) on an existing dwelling with existing communications systems ( CATV / Phone / satellite / random antennas ) those grounds should be moved to your new GES. There should be only one GES per structure, if any of the communications utilities drove their own little ground rod as they tend to do abandon that in favor of your new grounding system.
I don’t see anything from cattv/ phone/ satellite thankfully, but when they add it they will have a place to connect…
As far as the metal water pipe electrode, does it need to go all the way back to the service disconnect or can I make the connection at the three listed locations from post 5?
Since your drawing shows the service disconnect at another structure, and a GES is per structure so no.
If a large voltage difference develops between two grounding electrodes I don't want current flowing thru the electrical system to reach another electrode. Mike has some old videos on this discussing manufacturers that were advising people to add extra ground rods at their machines. The same concept applies to using the electrical system to connect electrodes.
I think its best for all bonding wires that make up a grounding electrode system; wires to the ground rod , water pipe electrode and inter system bonds land on a common busbar, but its not so much a 'code' concern and I think the way you drew it up your plan meets code.
Yes.
Yes.
Im wondering if the connection needs to originate from the emergency disconnect on the outside of the house or if it can originate from the sub panel down in the basement ?
The requirements I think are in 250.32(D), I think either is fine if the interior panel is "immediately inside".
That’s where I’m questioning if the basement panel will be compliant to run the gec wires out of.
the outside emergency disconnect feeds into a crawl space, pops into the basement, and hits a man lug panel. It’s not immediately inside but it’s the closest point inside. The basement panel is easier to get in and out. And whoever did the original install self tapped a couple lugs to the outside disconnect…. there is no room to run gec wires out of em disconnect. I planned on taking self tapper out and tapping a hole for a 1/4-20 and adding a double lug to fix the self tapper existing work.
Picture 1 is basement panel.
Picture 2 is em disconnect on outside
Picture 3 is the self tapped lug for emergency disconnects grounding lugs
I believe a separate structure requires its own ground electrode system. This means 2 rods if you are using rods unless you prove the one rod is 25 ohms or less. The water pipe doesn't change that, nor do I believe having 2 rods 75' away at a pole changes that.
Using the inside panel as the source for the GEC seems like a gray area. Be sure to use an EGC to the inside panel that is large enough to satisfy both 250.66 and 250.122 if you use the inside panel as the GEC source.