Understanding Continuous Loads

Merry Christmas
Status
Not open for further replies.

ndan305

Member
Location
Seattle, WA
Occupation
Engineer
Does the continuous load factor of 125% apply to motor loads and AC equipment?

For example:
I have a panel with:
1x AC unit, using MCA and MOP on nameplate
1x 2 hp motor, using 1.25*FLC
1x combination motor (2 hp and 1 hp motor), using 1.25*FLC largest motor + FLC smaller motor

The three loads are continuous loads that can operate more than 3 hours. Do I add up all the loads and add 25% on top of it to size my feeder conductors and panel breaker?

Then going on to service loads feeding the panel.. add another 25% on top of what we added up so far? It seems like safety factor on top of safety factor.

Panel load = total continuous load*1.25
Service load = panel load*1.25
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
The three loads are continuous loads that can operate more than 3 hours. Do I add up all the loads and add 25% on top of it to size my feeder conductors and panel breaker?
Add the FLC of all the motors, and add 25% of the largest motor.

That is the load on the panel. No additional adjustments needed.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Any HVAC equipment is a continuous load as far as i am concerned
The code tells you what a continuous load is. If it doesn't routinely run for 3 hours continuously it's not a continuous load. It would be very rare for any HVAC equipment to run continuously except in a case where somebody left the door open or something else unusual happened.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I wouldn't think all HVAC equipment is continuous load. If it takes 3 hours for your mechanical HVAC equipment to get back to your set-point, then something is wrong with your HVAC equipment.
I could see it if it's the first heating or cooling of the season of a vacant house.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
What does HVAC stand for?
Heating, ventilation, Air conditioning.
I would say it depends on each.
I know of ventilation that's runs non stop and some that runs as long as the business is open.
Now for a house I have wired air handlers that run 24/7 and the heat/ cool run so many cycles an hour.

My compressor on my AC unit had ran for more than three hours just before it Locke up. Then my wall unit ran untill it was fixed.
 