I have never seen a heat strip that was an even multiple of 5 kW for air handlers, They are almost always multiples of 4.8 kW. Unit heaters yes, I have seen and they almost always are in multiples of 5 kW, on ones that are larger than 5kW.
I agree but we call them 10kw-- my point is that the blower motors have increase in size or something because the units call for 56 amps.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't understand why that would anger an EC, if the job costs more you should make more not less.
It's a residential thing. :D

The problem is if you wired the units for 20 years with #6 and then you come back and find out that the wire demands a #4 then we eat it. It is just an added cost and we had to adjust but it cost many guys money because of this subtle change.
 