Hi all,
Question about a EVSE power management algorithm i'm observing for a three-phase panel.
Lets say a 600A rated panel has an EVSE Power Management policy to limit a group of chargers to 300A based on available capacity of the panel.
The way the software works is it takes the total specified power ceiling (300Amps) and divides that amongst the three phases so that the group of chargers on each phase will be limited to 100A (for load balancing purposes). I'm trying to understand if this makes sense versus having each phase support the full 300A.
The reason I'm asking is because based off my understanding, when filing out a panel schedule and balancing loads, the VA of each phase can total to the same VA rating of the entire panel and not just 1/3rd of it. For example, balancing a 300A 208V would allow each individual phase to have 108kVA (300x208x1.732) connected load.
Is this correct or is it proper to assume that each phase would only be able to handle 1/3rd of that number? If the latter, would the main breaker of the panel be at risk of tripping if a single phase was overloaded beyond 33%?