In my opinion, you are arguing for the sake of arguing. There are two ways of looking at NEC code: Absolute Wording or Intended Meaning. However, you are attempting to mix these two methods in an inappropriate manner in order to make an invalid point. :happysad:
Under Absolute Wording, this is not a parallel circuit and 310.4 does not apply (see Charlie's several postings as to why this is true).
Under Intended Meaning, neither conductor can ever be subjected to an amperage greater than its rating, so the purpose of 310.4 does not apply.
In your arguing for the sake of argument, argument, you are taking the non-absolute-wording approach in your definition of parallel conductors, but applying that to the absolute-wording of 310.4.
So in your opinion can you run 2 14AWG conductors from a 15 amp breaker to a receptacle? (most will say no you are paralleling the conductors). Yet many say add a second or even more receptacles and now this is not parallel conductors. What if you just added one receptacle and it happens to be in same enclosure as first (like a 2 gang box) and there is only 3 inches of conductor between the two receptacles. You have almost exactly the same thing.
Nobody is going to convince me that the two home runs are not parallel to each other. I agree they are not necessarily identical parallels but they are indeed parallel paths.
310.4 does not mention overcurrent protection. It just says conductors 1/0 and larger shall be permitted to be connected in parallel. Then parts B and C explain that they need to have same characteristics such as size, length, termination method, etc.
It is my opinion that the circuit in question does contain conductors that are connected in parallel, they are not the same length, and they are smaller than 1/0 AWG, therefore they are not allowed by 310.4. I also think it would be a better idea to just run a larger conductor in the first place if voltage drop is an issue.
Excepttion to 310.4(A) does allow conductors to be connected in parallel for instruments and control devices. This only makes sense. How can you get an "either/or" function out of dry contacts if you can't connect them in parallel?
Do I think there is a problem with using this setup? No. But I don't think it complies with 310.4.
I am not calling this "parallel conductors" I am calling it "conductors connected in parallel" which is the wording that is also used in 310.4
I totally disagree with the "
Absolute Wording or
Intended Meaning" theory you mention. The NEC says what it says. Absolute wording is part of the reason why the NEC is updated every three years. Sometimes the absolute wording is not interpreted the way the intended meaning was intended so three years later the absolute wording gets changed again. Intended meaning is simply reading it the way you (or somebody) want it to read. If absolute wording can be interpreted in more than one way than more than one way is what it means even if not intentional by the code making panel that wrote it, they have three more years to get it the way they wanted it.
As far as interpretation of what is written we have definitions in art 100 and we have definitions in some sections that apply to when a term is used in that section. If a word is not defined in either of those places then an english language dictionary is the source of a definition of a word. If there is more than one definition then there can be a problem. There is no definition of conductor in art 100. There also is no definition of parallel conductor there. 310.4 also does not use this terminology as I already mentioned above.