A freind was troubleshooting an 3 phase heater not working. It turned out one of the 3 "clips" on the panel bus had overheated on the push in Square D breaker(should have been an bolt on)....melted a bit of the bus away!
1) My thought was if it was an ungrounded Delta, is it possible a short was on one of the heater coils and drawing too much on one phase of the breaker?
2)If it was an existing ungrounded delta with a short on one phase, how do you meter it out?
3)I believe it was a 3 phase 4 wire system, but could bad bonding with a short on the one leg of the breaker for the heater have caused the "clip" on the bus to overheat and melt some of the bus? The breaker was moved, but i don't think they know what caused it yet...maybe a defective breaker? ...In defense of Square D, I know it could have been more than the 80% maunfacturers spec for warranty....will see if they checked the heater requirements.
Thanks again!
Thanks again!