Ungrounded DirecTV Dish System?
Hi Don:
So, if the dish and grounding block are more than 6 meters (20 feet) from the home's main electrical service entrance and main ground rod, a secondary ground rod is required for the dish and grounding block, but the two ground rods are NOT required to be bonded to each other?
I found the following regarding:
820.40(A)(4) - an exception has been added to permit a ground rod for the primary protector with a bonding connection to the power system electrode.
Doesn't that say the same thing I was saying? A 2ndary ground rod is needed at the dish and grounding block. The 2ndary ground rod must be bonded to the primary ground rod.
Part A4 also goes on to say "the grounding conductor shall be as short as practicable not to exceed 6.0 m (20 feet) in length. Exception: where it is it not practicable to achieve an overall max grounding conductor length of 6.0 m (20'), a separate ground as specified in 250.52 shall be used, the grounding conductor shall be grounded to the separate ground in accordance with 250.70 and the separate ground bonded to the power grounding electrode system in accordance with 820.40(D)."
Aren't I reading this correct?? Doesn't it say a 2ndary ground rod is required at the dish and ground block, then the two ground rods are required to be bonded to each other??
Please clear me up on this one. I thought I understood the code verbiage finally, but some of you are telling me otherwise. ;-)
Thanks.
Matt
Hi Don:
So, if the dish and grounding block are more than 6 meters (20 feet) from the home's main electrical service entrance and main ground rod, a secondary ground rod is required for the dish and grounding block, but the two ground rods are NOT required to be bonded to each other?
I found the following regarding:
820.40(A)(4) - an exception has been added to permit a ground rod for the primary protector with a bonding connection to the power system electrode.
Doesn't that say the same thing I was saying? A 2ndary ground rod is needed at the dish and grounding block. The 2ndary ground rod must be bonded to the primary ground rod.
Part A4 also goes on to say "the grounding conductor shall be as short as practicable not to exceed 6.0 m (20 feet) in length. Exception: where it is it not practicable to achieve an overall max grounding conductor length of 6.0 m (20'), a separate ground as specified in 250.52 shall be used, the grounding conductor shall be grounded to the separate ground in accordance with 250.70 and the separate ground bonded to the power grounding electrode system in accordance with 820.40(D)."
Aren't I reading this correct?? Doesn't it say a 2ndary ground rod is required at the dish and ground block, then the two ground rods are required to be bonded to each other??
Please clear me up on this one. I thought I understood the code verbiage finally, but some of you are telling me otherwise. ;-)
Thanks.
Matt