Paul,. Can you elaborate,. In particular why does pretty much every POCO disagree that delta-wye is the way to go?
Also, is there any reason a wye secondary couldn't be used? You could float the XO.
POCO is effectively three single phase systems except at a power plant. A delta wye feeds back voltage onto a missing phase in a single phase fault on the primary side. Wye wye is also slightly cheaper since primary insulation only has to be rated for line to ground voltage. Juxtapose that against true isolation of ground faults (separately derived system), harmonic mitigation, voltage unbalance mitigation, and elimination of circulating currents. These are all the reasons industrial plants prefer them.