18-16 Log #1396 NEC-P18 Final Action: Reject
(406.3(D))
________________________________________________________________
Submitter:
George Stolz, II, Pierce, CO
Recommendation:
Add new text to read:
(D) Replacement. Replacement of receptacles shall comply with 406.3(D)(1), (2), and (3) as applicable. Receptacles installed to additions to existing branch circuits shall be considered replacements for the purpose of this section.
Substantiation:
The section in question (406.3(D)) effectively bends the standard requirements for new installations to provide relief for the installer when dealing with old work. Given the leniency put forth by this section regarding replacement receptacles, it appears that old 2-wire installations, while regrettable, do not present an ?imminent danger to occupants? as stated in 80.5(B).
80.5(C) expresses that ?Additions...shall not cause a building to become unsafe...?. By expressing explicit guidelines for additions to existing circuits, installers will be forbidden to connect an unbonded EGC between receptacles, decreasing the shock hazard in the event of an unbonded fault. In many cases, these existing circuits are extended to add receptacles to conform with 210.52.
The elimination of extension cord use should carry nearly as much importance as EGC?s in this environment.
Panel Meeting Action: Reject
Panel Statement:
Section 406.3(D) addresses the installation of replacement receptacles. This proposal addresses the installation of new receptacles. Therefore, this text does not apply to this section. The panel rejects the concept of adding new receptacles to an existing two-wire circuit and applying the provisions for replacement receptacles rules. Replacement receptacles rules are to increase the safety of older two-wire branch circuits where a replacement receptacle is desired. Section 406.3(D)(3) does not address the extension of existing two-wire circuits. The applicable rules for extending two-wire branch circuits are contained in Section 250.130(C) and require the extension to provide an equipment grounding conductor. The references to Sections 80.5(B) and 80.5(C) are now contained in Annex G of the 2005 NEC as 80.9(B) and (C). Annex G is not enforceable unless specifically adopted by local ordinance.
Number Eligible to Vote: 12
Ballot Results:
Affirmative: 12