ungrounded receptacles

Status
Not open for further replies.
Re: ungrounded receptacles

Under the NEC yes you can.

Check out 406.3(D)(3).

However 250.114 is also worth a look to see all the items you will not be able to plug in to that ungrounded receptacle. :p
 
Re: ungrounded receptacles

:)
Originally posted by stew:
thx guys didnt have the book and couldnt remeber. senior moments come more frequently now.
:D :D Back in 1959 when I was a senior in high school, I had several wonderful senior moments.

Are you still in HS or are you now a college senior.

Never mind i forgot what I wanted to say. :D :D
 