77401
Banned
georgestolz said:A lot of installers have no idea what the EGC is supposed to do. Is Joe Homeowner going to know what the fancy receptacle means?
Good point, probably no more than a sticker.
In that case, you did not add a metal box, the metal box was already there - so no action is required, IMO.bjp_ne_elec said:In a replacement situation, how do you deal with metal boxes. Metal boxes shall be bonded to the equipment grounding conductor - but what about in this situation.
IMO, yes, because the boxes are existing.Also, someone mentioned needing to add a ground if you "add to the circuit". Can you "subtract from the circuit" - in other words disconnect some branches off of it, and still leave the ungrounded metal boxes installed?
About the closest thing would be Article 80, which is unenforceable unless adopted.Have struggled with this "twist", and would really like someone to point to a code reference that clarifies this "twist".
First, the new romex to the new first box in the circuit would not require GFCI protection unless otherwise required for the area (as in, 210.8), because this box would have an EGC.Here's another "twist" - can I bring a new grounded Romex to the first box, install a GFCI in the new box, and leave the rest of the circuit "as is" - which would be non-grounded receptacles and could include metal JB's - which are obviously non-grouned - as no ground exists in the existing Romex.