Section 690.47 ?Grounding Electrode System?
This section includes some relatively minor revisions for clarity, as well as one major addition that some Code experts have condemned as unsafe.
Ungrounded PV systems. In prior Code cycles, there was some confusion regarding grounding-electrode conductors for ungrounded systems. Section 690.47(B) now specifically allows use of an ac equipment-grounding system as the ground-fault?detection reference for ungrounded PV systems. In addition, Section 690.47(C)(3) states that a combined dc grounding-electrode conductor (GEC) and ac equipment-grounding conductor (EGC) can be installed for ungrounded systems. This combined dc GEC and ac EGC is sized in accordance with Section 250.122?as an EGC, in other words?and is not required to be larger than the largest ungrounded phase conductor. Note that this combined grounding conductor must still be unspliced or irreversibly spliced.
As an example, if a non-isolated inverter?s ac output circuit back-feeds a 30 A circuit breaker, the combined dc GEC and ac EGC between the inverter and the service panel can be sized per Table 250.122, which specifies 10 AWG copper based on the OCPD rating. Further, the combined dc GEC and ac EGC is never required to be larger than the ungrounded phase conductors of the PV system. This allows the combined grounding conductor to be sized smaller than the minimum dc GEC size of 8 AWG that Section 250.166 would otherwise require. When these sections are applied together, it is clear that non-isolated (transformerless) inverters used in ungrounded PV systems do not require a dc GEC sized per Section 250.166 to be run to a dc grounding electrode. Instead, an unspliced conductor acting as the ac EGC can be used to meet the grounding electrode system requirements for ungrounded PV systems.