Re: uninsulated overhead grounded conductor
The only way this might not be true is as Don mentioned the building has a metal water main interconnected with the neighbors bonded metal water main.
Think of a house fed from a well or a plastic water main, it has a uffer and a ground rods, break just the neutral from the utility.
There will now be dangerous potential between any bonded surfaces and the 'earth'.
You would get blasted standing on damp ground while touching the meter socket or an outside faucet.
The grounding electrodes can not eliminate this difference of potential.
Properly grounded or not the structure side of a broken grounded conductor will be at a dangerous potential to ground if one or more of the ungrounded conductors is intact.Originally posted by rattus:
when I say "grounded", I mean properly grounded.
The only way this might not be true is as Don mentioned the building has a metal water main interconnected with the neighbors bonded metal water main.
Think of a house fed from a well or a plastic water main, it has a uffer and a ground rods, break just the neutral from the utility.
There will now be dangerous potential between any bonded surfaces and the 'earth'.
You would get blasted standing on damp ground while touching the meter socket or an outside faucet.
The grounding electrodes can not eliminate this difference of potential.