The question is: "What's the maximum size overcurrent protection device for a 2,500 W, 240 V water heater?"
The possible answers are (a) 15 A, (b) 20 A, (c) 30 A, or (d) none of these.
I selected (b) 20 A, but the answer key gives (a) 15 A. I think that the key might be wrong.
422.11(E) Single Non–Motor-Operated Appliance reads as follows:
I think that (1) does not help because the OCPD size is not marked on the appliance, (3) should not apply because the appliance is not rated at more than 13.3 A (2,500 W ÷ 240 V = 10.42 A), and (2) should apply because the appliance is rated at less than 13.3 A. Therefore, I think that the answer should be (b) 20 A.
Am I missing something here?
If the branch circuit supplies a single non–motor-operated appliance, the rating of overcurrent protection shall comply with the following:
(1) Not exceed that marked on the appliance.(2) Not exceed 20 amperes if the overcurrent protection rating is not marked and the appliance is rated 13.3 amperes or less; or(3) Not exceed 150 percent of the appliance rated current if the overcurrent protection rating is not marked and the appliance is rated over 13.3 amperes. Where 150 percent of the appliance rating does not correspond to a standard overcurrent device ampere rating, the next higher standard rating shall be permitted.