Good evening,
I just received a sketch from the architect/engineer for 120v receptacles to be installed under a raised floor assembly. Here's the catch; We are to install a
4"x4" trough right down the center of the underfloor space, then come out of the trough with 20' lengths of MC with a receptacle mounted in a Handy box at the end. It seems there intention is to be able to move the receptacles to where power is needed, but a few code issues come to mind. The box needs to be secured, no? The MC needs to be secured and supported. Hard usage cord with strain relief and a pendant style box seems more appropriate. Any input?
Thanks people...
Charles
I just received a sketch from the architect/engineer for 120v receptacles to be installed under a raised floor assembly. Here's the catch; We are to install a
4"x4" trough right down the center of the underfloor space, then come out of the trough with 20' lengths of MC with a receptacle mounted in a Handy box at the end. It seems there intention is to be able to move the receptacles to where power is needed, but a few code issues come to mind. The box needs to be secured, no? The MC needs to be secured and supported. Hard usage cord with strain relief and a pendant style box seems more appropriate. Any input?