joe tedesco
Senior Member
- Location
- Boston, Massachusetts
Is Support Required Here?
Is Support Required Here?
Is Support Required Here?
How so? Under the 2005 code it requires support and also under the new rule in the 2008 code because it has a coupling. The new rule requires that the conduit be "unbroken" if you want to delete the supports.If you leave the code alone, it will not require support.
don_resqcapt19 said:Ryan,
How so? Under the 2005 code it requires support and also under the new rule in the 2008 code because it has a coupling. The new rule requires that the conduit be "unbroken" if you want to delete the supports.
Don
joebell said:I'm confussed, why would this need to be supported in the 2005 code if the distance between to two disconnects is less the 3 feet or is the key word I am missing "within"?
Yes the new rule is less stringent, but I wonder about enforcement now that we have a rule. In many areas the inspectors were permitting what you proposed, even though it was a violation.Although I don't like what CMP 8 did to this proposal, it is still less stringent than the code was before.
ryan_618 said:Because there is no support...CMP 8 has routinely stated that raceway connectors are not a point of support. With that said, every installation of conduit that didn't have a support was a violation.
Although I don't like what CMP 8 did to this proposal, it is still less stringent than the code was before.