Re: Unsure of Wire Size
I do not have to make an educated guess.
If I have to deal with a 50% downward adjustment I can just add 200% (the inverse of 50% down)
I needed a conductor that was permissible to use on a 30 amp circuit, 30 + 200% = 60 amps that means a 6 awg.
To take from a recent thread here what size conductors and OCP does a fixed load of 900 amps need.
[ December 01, 2003, 03:27 PM: Message edited by: iwire ]
The results are not the same, I come up with a 6 awg for the application and you came up with 8 awg.Originally posted by itasca_mn:
The results are the same, except that we are approaching it from opposite directions. Using your approach you must use an educated guess at a conductor size, and derate its ampacity.
I do not have to make an educated guess.
If I have to deal with a 50% downward adjustment I can just add 200% (the inverse of 50% down)
I needed a conductor that was permissible to use on a 30 amp circuit, 30 + 200% = 60 amps that means a 6 awg.
Yes and you also have to figure in your breaker size.Except for general purpose branch circuits where exact loads are impossible to pin down, you always base conductor size on the load being served.
To take from a recent thread here what size conductors and OCP does a fixed load of 900 amps need.
[ December 01, 2003, 03:27 PM: Message edited by: iwire ]