Unused neutral in a subpanel for a DELTA system
makes a great place to land EGC's, I've even done that with wye systems where the neutral isn't going to be utilized.
kwired: I'm just trying to figure out how you do this. Do you then just install a jumper (bonding conductor) between the neutral bar and equipment ground bar? If yes, how do you size that jumper (bonding conductor)?
Usually that jumper comes with the panelboard for applications where it is a service disconnect / main panel. If I need a wire jumper to use the unused neutral bar as an EGC in a subpanel, I'd based it off of Table 250.122 and match the main supply.
+1. Usually am not installing any equipment ground bars either, just put in the bonding jumper for the neutral assembly.
Thank you guys!