Unusual Circuit Breaker

Merry Christmas
It would help if we saw the configuration of the back, but the tan handle suggests that it could be a Cutler-Hammer classic circuit breaker.
Thank you for the reply. It is for a Cutler Hammer panel. I ordered a 2-pole 60 amp breaker and this is what they sent. It is a 2-pole breaker, but it has 30 amps on one pole and 60 on the other. The only use I can think of would be for something that needs 2 different 120 volt loads that would share a neutral. Something like a machine with two different size motors.
 
Well if one side is actually 30A and given the fact it's common trip it would never carry a 60 amp load period. 😉
 
Here's another one, we found it in a remodel project once. It was really a 100 amp two pole with a factory mistake handle.

1766439988306.png
 
Won't see that with a QO breaker as they have a single handle and internal tie to the other pole(s)
But 40 years ago I touched a 3 pole QO with 2 plug-on and 1 bolt-on connections. And, that was back when plug-on and bolt-on used different panels.
 
Top