I have a 112.5 KVA 277/480 primary, 120/240 secondary. I have 277/480 going in (double checked, all legs are the same around 277) but for the secondary, I have 120 on black, 212 on red, and 120 on blue (hot to ground). All line to line read around 240 though. Has anybody ever ran into this? I don't know why I have 212 on red. Taps are all set the same to 480 volts. Also, I know some transfomers hum pretty loud, but it seems to be humming a little louder than normal. Any feedback would be appreciated.
Thanks.
212 Volts is not to far out of the ordinary for the B phase of a 120/240 volt delta wound secondary, mathematically it should be 208 volts ( 120 x 1.732). As far as the loud humming goes, have you tried loosening the rubber mounting straps slightly? a lot of manufacturer's tighten them down pretty snug for shipping purposes. If that doesn't quiet it down any, try putting rubber/cork isolation pads under the mounts on the feet of the transformer.
I agree 3?, 4W Delta because you couldn't have 120/240 with a WYE secondary. What does the nameplate say?
If you want 120V to neutral on all three phases you would need a 480V x 208Y/120V transformer. Which would give you 208V line to line.