romex jockey
Senior Member
- Location
- Vermont
- Occupation
- electrician
so would one check with the neighbors to verify this?If the voltage offset is present with the main breaker off and there is not a metal water pipe connection to another customer, a strong possiblity is that POCO has lost their metallic multiply grounded neutral (MGN) connection on the primary side of their transformer. The unbalanced primary currrent flowing through their local earth electrodes causes an offset of voltage between the secondary neutral and earth ground.
This potentially a very dangerous situation and would have to be corrected by POCO. If it is not an actual break but just a marginally sized primary neutral, POCO may want to insert a ground isolator on the customer's neutral instead of actually fixing the problem. 14 volts is more than is usually appropriate for a ground isolator.
~RJ~