Unusual Use for an MTS?

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
An existing 100 amp load is supplied by a 3-phase 100 amp breaker. A new 100 amp load is being installed. The system can't handle the load of both the existing and the new at the same time, and there will never be a need to run them both at the same time. What do you think about using a Manual Transfer Switch to select which load will get power and be allowed to operate?
 
An existing 100 amp load is supplied by a 3-phase 100 amp breaker. A new 100 amp load is being installed. The system can't handle the load of both the existing and the new at the same time, and there will never be a need to run them both at the same time. What do you think about using a Manual Transfer Switch to select which load will get power and be allowed to operate?

sounds workable to me
 
Keep in mind if there if any type controller such as a motor starter/contactor is involved you might accomplish the same thing by use of a selector switch in the control circuits.
 
Might be able to be accomplished with a breaker interlock device. Those are sometimes used for residential generator interlock purposes.
 
I haven't visited the site yet. I may be able to do that next week. There is a question of whether the panel has room for an additional 100 amp breaker. So the thought is to intercept the existing branch circuit from the panel's 100 amp breaker (serving an electric unit heater), insert the MTS, and run the other side of the MTS to the new 100 amp load (a heat pump). Sounds like it is a viable option. Thanks for the comments.
 
I haven't visited the site yet. I may be able to do that next week. There is a question of whether the panel has room for an additional 100 amp breaker. So the thought is to intercept the existing branch circuit from the panel's 100 amp breaker (serving an electric unit heater), insert the MTS, and run the other side of the MTS to the new 100 amp load (a heat pump). Sounds like it is a viable option. Thanks for the comments.

Funny that you've mentioned a unit heater, we recently had a room that stored the building window washing unit that they wanted to heat during the winter. Since getting a new circuit there was nearly impossible we intercepted the washer circuit and installed a 100 amp MTS. During the winter months when the window washer isn't used the building engineer switches from washer to unit heater. :cool:
 