Upgrading a subpanel

Status
Not open for further replies.

GeorgeW

Member
I am trying to find some guidance on the following: I have a customer who will be moving a small chiropractic business into a building that has two apartments on the second floor, and office space on the first. The main service is 200 amp, single phase, 3 wire. There is one subpanel for an apartment that has a 50 amp disconnect (breaker), one has a 30 amp disconnect (two 30 amp fuses in parrallel) and finally the panel my customer will be using is a 100 amp disconnect. She needs to have a 60 amp two pole breaker added for an x ray machine. My question...can I safely and legally upgrade her panel to 150 amp disconnect? I cannot find any clear guidance in the NEC.
 
I am trying to find some guidance on the following: I have a customer who will be moving a small chiropractic business into a building that has two apartments on the second floor, and office space on the first. The main service is 200 amp, single phase, 3 wire. There is one subpanel for an apartment that has a 50 amp disconnect (breaker), one has a 30 amp disconnect (two 30 amp fuses in parrallel) and finally the panel my customer will be using is a 100 amp disconnect. She needs to have a 60 amp two pole breaker added for an x ray machine. My question...can I safely and legally upgrade her panel to 150 amp disconnect? I cannot find any clear guidance in the NEC.

You can upgrade all you want as long as the total load does not exceed 200 amps. You need to calculate the loads.
 
?
and finally the panel my customer will be using is a 100 amp disconnect. She needs to have a 60 amp two pole breaker added for an x ray machine. My question...can I safely and legally upgrade her panel to 150 amp disconnect? I cannot find any clear guidance in the NEC.

You should calculate the load see Article 220 and examples in the Annex. The breaker amperes don?t play a role in feeder/service size, the calculated load does. The calculated load qualifies the ampere size for service, feeder, & distribution.

You can install a larger ampere panel or service and under-serve or supply it. Many installations need breaker quantity and lower ampere subpanels are limited with low quantity spaces.
 