UPS’s inverter output current issue

Status
Not open for further replies.

SoonIWill

New User
Location
KSA
Occupation
Operator
Hi

I have UPS 50KVA and the inverter output AC voltage is feeding a distribution panel 120/208 V 4 wires when I check UPS display it shows me that output current which is the distribution panel phases as followings phase one = 30A while Phase 2 = 0A and phase 3 = 0A is this a problem !? Shall we work to make the load almost shared on all 3 phases not only one !?
 
Hi

I have UPS 50KVA and the inverter output AC voltage is feeding a distribution panel 120/208 V 4 wires when I check UPS display it shows me that output current which is the distribution panel phases as followings phase one = 30A while Phase 2 = 0A and phase 3 = 0A is this a problem !? Shall we work to make the load almost shared on all 3 phases not only one !?
If you add any single pole loads make sure to put them on phase 2 (B) or phase 3 (C) that will help balance.
 