vicdog

Member
Hi Guys. Just wanted to see if anyone had input on sizing battery conductors. I typically size them per standard NEC rules but consistently see them undersized. For instance: 2000amp breaker, four sets of 500mcm (4+, 4-) in EMT. Is there something hiding in the code that I'm missing?

Thanks for the input.
 

Finite10

Senior Member
Location
Great NW
480.4 covers protection of conductors from batteries under 50V.
The seemingly undersized conductors may be part of; listed, labelled, or approved for the application equipment/materials.

No real help, I know.
 