Question about designing the branch circuit for a UPS that is capable of a 3000VA/2250W output. I calculate that the UPS will draw 25A (3000VA/120V). To size the conductors and breaker, I multiply the 25A by 125% because it is a continuous load. This results in a 31.25A load. The next size breaker is 35A. However, the input connection for the UPS is a L5-30R, which is only rated for 30A.
Is the 30A receptacle protected by the 35A breaker? If not, how do I resolve this issue.