UPS Charging current

Status
Not open for further replies.

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
Do we need to size the ups upstream breaker so that it's rated to the UPS FLC + Batteries charging current?
 
Do we need to size the ups upstream breaker so that it's rated to the UPS FLC + Batteries charging current?
We do exactly what the installation manual says. From overcurrent/short circuit protection to wire size to input and output being in separate raceways.
 
We do exactly what the installation manual says. From overcurrent/short circuit protection to wire size to input and output being in separate raceways.
I am preparing the tender documents, so it is pre installation.
 
If the UPS always supplies power to the load, even with normal power on, then the power supply to the UPS will have to support both the actual load and the battery charging load. That way when normal power is restored, the supply circuit can supply both the actual load and the battery charging load.
 