UPS Charging current

Status
Not open for further replies.

m sleem

Exemplary Сasual Dating - Genuine Females
Location
Usa
Occupation
Health
Do we need to size the ups upstream breaker so that it's rated to the UPS FLC + Batteries charging current?
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Do we need to size the ups upstream breaker so that it's rated to the UPS FLC + Batteries charging current?
We do exactly what the installation manual says. From overcurrent/short circuit protection to wire size to input and output being in separate raceways.
 

m sleem

Exemplary Сasual Dating - Genuine Females
Location
Usa
Occupation
Health
We do exactly what the installation manual says. From overcurrent/short circuit protection to wire size to input and output being in separate raceways.
I am preparing the tender documents, so it is pre installation.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If the UPS always supplies power to the load, even with normal power on, then the power supply to the UPS will have to support both the actual load and the battery charging load. That way when normal power is restored, the supply circuit can supply both the actual load and the battery charging load.
 
Status
Not open for further replies.
Top